Eu sempre ouvi 40%, apesar de não poder fazer o backup. Eu vou dizer que você precisa de umidade alguns para reduzir o acúmulo de eletricidade estática.
EDITAR:
Ah, achei minha documentação, boa parte da Sun Microsystems nº 805-5863-13, "Guia de Planejamento de Locais do Centro de Dados da Sun Microsystems: Melhores Práticas de Data Centers"
Temperature and relative humidity conditions should be maintained at levels that allow for the greatest operational buffer in case of environmental support equipment down-time. The goal levels for the computer room should be determined in a manner that will achieve the greatest operational buffer and the least possibility of negative influence. The specific hardware design, room configuration, environmental support equipment design and other influencing factors should be taken into consideration when determining the specific relative humidity control appropriate for a particular room. Psychrometrics can affect hardware through thermal influences, Electrostatic Discharge (ESD), and increases in environmental corrosivity.
E:
Under most circumstances, air conditioners should be set at 72º F (22º C) with a sensitivity range of +/- 2º F (+/-1º C). Humidifiers, in most cases, should be set at 48% RH with a sensitivity range of +/- 3% RH. The set-points of the air conditioners should always be chosen in an effort to maintain the optimal recommended temperature and relative humidity levels for the room environment. These set points should maintain appropriate conditions, while allowing wide enough sensitivity ranges to help avoid frequent cycling of the units. While these tight ranges would be difficult to maintain in a loosely controlled office environment, they should be easily attained in a controlled data center.
Numerous factors, such as heat-load and vapor barrier integrity, will influence the actual set-points. If the room lacks adequate vapor barrier protection, for instance, it may be necessary to adjust humidifier set points to accommodate seasonal influences. Ideally, all inappropriate influences on the data center environment will be eliminated, but in the event that they are not, minor adjustments, made by trained personnel, can help alleviate their effects on the environment.
E na descarga eletrostática:
The maintenance of appropriate relative humidity levels is probably the most universal and easiest means of addressing ESD concerns. Appropriate moisture levels will help ease the dissipation of charges, lessening the likelihood of catastrophic failures. The following chart illustrates the effect moisture levels can have on electrostatic charge generation. Note – Source Simco, A Basic Guide to an ESD Control Program for Electronics Manufacturers
TABLE 6-3 Electrostatic Voltage At Workstations
Static Voltage
Means Of Static Generation Relative Humidity 10-20% Relative Humidity 65-90%
Walking Across Carpet 35,000 1,500
Walking over vinyl floor 12,000 250
Worker at bench 6,000 100
Vinyl envelopes for work instructions
7,000 600
Common polly bag picked up from bench
20,000 1,200
Work chair padded with urethane foam
18,000 1,500